The insulation should make contact with both skins of sheeting. See also Diagram 5.2a regarding the need for fire-stopping where such roofs pass over the top of a compartment wall. See para 8.
All compartment walls and compartment floors should achieve both of the following. a. Form a comple...
Cavity barriers should be tightly fitted to a rigid construction and mechanically fixed in position....
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
Cavity barriers are not required between double-skinned corrugated or profiled insulated roof sheeti...
a. ANY BUILDING OR COMPARTMENT Roof covering over this distance to be designated BROOF(t4) rated on...
A compartment wall should achieve both of the following. a. Meet the underside of the roof covering...
Fire-stopping (same resistance as compartment) Cavity barriers NOTE: 1. See paragraph 8.5 See pa...
See para 2.5 Alternative cavity barrier arrangements in roof space over protected stairway in a hou...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
To reduce the potential for fire spread, cavity barriers should be provided for both of the followin...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
The construction enclosing a protected shaft (Diagram 7.1) should do all of the following. a. Form ...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
All compartment walls and compartment floors should achieve both of the following. a. Form a comple...
Cavity barriers should be tightly fitted to a rigid construction and mechanically fixed in position....
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
Cavity barriers are not required between double-skinned corrugated or profiled insulated roof sheeti...
a. ANY BUILDING OR COMPARTMENT Roof covering over this distance to be designated BROOF(t4) rated on...
A compartment wall should achieve both of the following. a. Meet the underside of the roof covering...
Fire-stopping (same resistance as compartment) Cavity barriers NOTE: 1. See paragraph 8.5 See pa...
See para 2.5 Alternative cavity barrier arrangements in roof space over protected stairway in a hou...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
To reduce the potential for fire spread, cavity barriers should be provided for both of the followin...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
The construction enclosing a protected shaft (Diagram 7.1) should do all of the following. a. Form ...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
All compartment walls and compartment floors should achieve both of the following. a. Form a comple...
Cavity barriers should be tightly fitted to a rigid construction and mechanically fixed in position....
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...