NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific performance in relation to fire resistance. 2. Domestic meter cupboards may be installed provided that the following conditions are met: a. There are no more than two cupboards per dwelling b. The openings in the outer wall leaf are not bigger than 800X500mm for each cupboard c. The inner leaf is not penetrated except by a sleeve not more than 80X80mm, which is fire-stopped. 3. Materials achieving class B-s3, d2 or worse may be placed within the cavity. See para 8.
The external wall of a protected shaft does not normally need to have fire resistance. Situations wh...
a. Flue passing through compartment wall or floor b. Flue built into compartment wall Flue walls s...
Fire doorsets often do not provide any significant insulation. Unless providing both integrity and ...
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
Fire-stopping (same resistance as compartment) Cavity barriers NOTE: 1. See paragraph 8.5 See pa...
To reduce the potential for fire spread, cavity barriers should be provided for both of the followin...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Openings should be limited to the following. a. Fire doorsets with a minimum E 30 rating, fitted in...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Cavity barriers should be fixed so their performance is unlikely to be made ineffective by any of th...
In a statistical study performed by the London fire brigade in the Real Fires Database it was found ...
To build multi story buildings out of timber is of a common interest in the building sector. Timber ...
Light gauge steel framed (LSF) walls are used in fire compartmentation to prevent the spread of fire...
The external envelope of a building should not provide a medium for fire spread if it is likely to b...
NOTE: The ceiling should meet the following conditions. a. Provide a minimum fire resistance of EI...
The external wall of a protected shaft does not normally need to have fire resistance. Situations wh...
a. Flue passing through compartment wall or floor b. Flue built into compartment wall Flue walls s...
Fire doorsets often do not provide any significant insulation. Unless providing both integrity and ...
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
Fire-stopping (same resistance as compartment) Cavity barriers NOTE: 1. See paragraph 8.5 See pa...
To reduce the potential for fire spread, cavity barriers should be provided for both of the followin...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Openings should be limited to the following. a. Fire doorsets with a minimum E 30 rating, fitted in...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Cavity barriers should be fixed so their performance is unlikely to be made ineffective by any of th...
In a statistical study performed by the London fire brigade in the Real Fires Database it was found ...
To build multi story buildings out of timber is of a common interest in the building sector. Timber ...
Light gauge steel framed (LSF) walls are used in fire compartmentation to prevent the spread of fire...
The external envelope of a building should not provide a medium for fire spread if it is likely to b...
NOTE: The ceiling should meet the following conditions. a. Provide a minimum fire resistance of EI...
The external wall of a protected shaft does not normally need to have fire resistance. Situations wh...
a. Flue passing through compartment wall or floor b. Flue built into compartment wall Flue walls s...
Fire doorsets often do not provide any significant insulation. Unless providing both integrity and ...