Compartment walls in a top storey beneath a roof should be continued through the roof space
Compartment walls should be able to accommodate deflection of the floor, when exposed to fire, by ei...
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
See para 2.5 Alternative cavity barrier arrangements in roof space over protected stairway in a hou...
Adjoining buildings should only be separated by walls, not floors. Compartment walls common to two o...
Compartment walls not described in paragraphs 7.8 and 7.9 should run the full height of the storey i...
A compartment wall should achieve both of the following. a. Meet the underside of the roof covering...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
Dwellinghouses that are semi-detached or in terraces should be considered as separate buildings. Eve...
a. ANY BUILDING OR COMPARTMENT Roof covering over this distance to be designated BROOF(t4) rated on...
All of the following should be provided as compartment walls and compartment floors and should have,...
Timber beams, joists, purlins and rafters may be built into or carried through a masonry or concrete...
Parts of a building occupied mainly for different purposes should be separated from one another by c...
The insulation should make contact with both skins of sheeting. See also Diagram 5.2a regarding the ...
Compartment walls should be able to accommodate deflection of the floor, when exposed to fire, by ei...
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
See para 2.5 Alternative cavity barrier arrangements in roof space over protected stairway in a hou...
Adjoining buildings should only be separated by walls, not floors. Compartment walls common to two o...
Compartment walls not described in paragraphs 7.8 and 7.9 should run the full height of the storey i...
A compartment wall should achieve both of the following. a. Meet the underside of the roof covering...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
Dwellinghouses that are semi-detached or in terraces should be considered as separate buildings. Eve...
a. ANY BUILDING OR COMPARTMENT Roof covering over this distance to be designated BROOF(t4) rated on...
All of the following should be provided as compartment walls and compartment floors and should have,...
Timber beams, joists, purlins and rafters may be built into or carried through a masonry or concrete...
Parts of a building occupied mainly for different purposes should be separated from one another by c...
The insulation should make contact with both skins of sheeting. See also Diagram 5.2a regarding the ...
Compartment walls should be able to accommodate deflection of the floor, when exposed to fire, by ei...
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
See para 2.5 Alternative cavity barrier arrangements in roof space over protected stairway in a hou...