To reduce the potential for fire spread, cavity barriers should be provided for both of the following. a. To divide cavities. b. To close the edges of cavities. Cavity barriers should not be confused with fire-stopping details (Section 9)
In addition to any other provisions in this section, both of the following conditions should be met....
At the junction with another compartment wall or an external wall, the fire resistance of the compar...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
To reduce the potential for fire spread, cavity barriers should be provided for both of the followin...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Fire-stopping (same resistance as compartment) Cavity barriers NOTE: 1. See paragraph 8.5 See pa...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Openings should be limited to the following. a. Fire doorsets with a minimum E 30 rating, fitted in...
In divided corridors (paragraph 3.25 and following) with cavities, fire-stopping should be provided ...
Cavity barriers should be tightly fitted to a rigid construction and mechanically fixed in position....
In a statistical study performed by the London fire brigade in the Real Fires Database it was found ...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
Cavity barriers should be provided in accordance with Section 5 in dwellinghouses and Section 8 in f...
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
In addition to any other provisions in this section, both of the following conditions should be met....
At the junction with another compartment wall or an external wall, the fire resistance of the compar...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
To reduce the potential for fire spread, cavity barriers should be provided for both of the followin...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Fire-stopping (same resistance as compartment) Cavity barriers NOTE: 1. See paragraph 8.5 See pa...
Cavity barriers should be provided at all of the following locations. a. At the edges of cavities, ...
Openings should be limited to the following. a. Fire doorsets with a minimum E 30 rating, fitted in...
In divided corridors (paragraph 3.25 and following) with cavities, fire-stopping should be provided ...
Cavity barriers should be tightly fitted to a rigid construction and mechanically fixed in position....
In a statistical study performed by the London fire brigade in the Real Fires Database it was found ...
It is not appropriate to complete a line of compartment walls by fitting cavity barriers above them....
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
Cavity barriers should be provided in accordance with Section 5 in dwellinghouses and Section 8 in f...
NOTES: 1. Materials used to close the cavity in this arrangement do not need to achieve a specific ...
In addition to any other provisions in this section, both of the following conditions should be met....
At the junction with another compartment wall or an external wall, the fire resistance of the compar...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...