A vent to the outside with a minimum free area of 1m2 should be provided from the top storey of the stair
Divide a common corridor connecting two or more storey exits with a fire doorset fitted with a self-...
The subject of venting, that is of providing openings to release the heat and smoke of building fire...
Elevator shaft and stairwell shaft pressurization systems are studied as means of smoke migration pr...
Smoke vents should comply with one of the following. a. They should be located on an external wall ...
Despite the provisions described, it is probable that some smoke will get into the common corridor o...
The combined clear cross-sectional area of all smoke outlets should be a minimum of 1/40 of the area...
Guidance on the design of smoke control systems that use pressure differentials is available in BS E...
Air movement caused by stack action can be an important means by which smoke spreads from floor to f...
In the event of a fire, smoke migrates from the fire floor to upper floors mainly through vertical s...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
Where a stair serves an enclosed car park or place of special fire hazard, the lobby or corridor sho...
Heat and smoke from basement fires vented via stairs can inhibit access for firefighting personnel. ...
Buildings are evolving in height, construction materials, use, and compartmental composition at sta...
Details requirements, test methods and labelling for natural smoke and heat exhaust ventilators, to ...
All of the following precautions should be taken to avoid the spread of smoke and fire to the protec...
Divide a common corridor connecting two or more storey exits with a fire doorset fitted with a self-...
The subject of venting, that is of providing openings to release the heat and smoke of building fire...
Elevator shaft and stairwell shaft pressurization systems are studied as means of smoke migration pr...
Smoke vents should comply with one of the following. a. They should be located on an external wall ...
Despite the provisions described, it is probable that some smoke will get into the common corridor o...
The combined clear cross-sectional area of all smoke outlets should be a minimum of 1/40 of the area...
Guidance on the design of smoke control systems that use pressure differentials is available in BS E...
Air movement caused by stack action can be an important means by which smoke spreads from floor to f...
In the event of a fire, smoke migrates from the fire floor to upper floors mainly through vertical s...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
Where a stair serves an enclosed car park or place of special fire hazard, the lobby or corridor sho...
Heat and smoke from basement fires vented via stairs can inhibit access for firefighting personnel. ...
Buildings are evolving in height, construction materials, use, and compartmental composition at sta...
Details requirements, test methods and labelling for natural smoke and heat exhaust ventilators, to ...
All of the following precautions should be taken to avoid the spread of smoke and fire to the protec...
Divide a common corridor connecting two or more storey exits with a fire doorset fitted with a self-...
The subject of venting, that is of providing openings to release the heat and smoke of building fire...
Elevator shaft and stairwell shaft pressurization systems are studied as means of smoke migration pr...