An investigation was carried out to find the most optimum configuration, particularly the torque matching characteristics, of an integrated Revolving Vane compressor- expander. To carry out the study, a mathematical model of the integrated compressor-expander was developed. An open cycle air refrigeration system was adopted. The controlled parameter was the angle shift between the compressor and the expander. The observed parameters were the peak torque requirement and the bearing load. The results show that when properly matched, the peak torque can be reduced by more than 65% while the bearing loads can be reduced by up to 25%, depending on operating conditions. Unfortunately, the optimum angle shifts for peak torque do not always coincid...