The flights and landings of escape stairs should be constructed of materials achieving class A2-s3, d2 or better in all of the following situations. a. If the escape stair is the only stair in a building with more than three storeys. b. If the escape stair is within a basement storey. c. If the escape stair serves any storey that has a floor level more than 18m above ground or access level. d. If the escape stair is an external escape stair, except where the stair connects the ground storey or ground level with a floor or flat roof a maximum of 6m above or below ground level. e. If the escape stair is a firefighting stair. Materials achieving class B-s3, d2 or worse may be added to the top horizontal surface, except on firefighting st...
Where a storey or part of a building has multiple escape routes available, one may be over a flat ro...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
Buildings in which firefighting shafts should be provided, showing which storeys need to be served ...
Any external escape stair should meet all of the following conditions (Diagram 3.11). a. Doors to t...
If a building does not meet the criteria of paragraph 3.28, an escape stair forming part of the only...
Dwellinghouses with one internal stair should comply with paragraphs 2.5 and 2.6. In dwellinghouses ...
Further guidance on the construction of firefighting stairs is given in Section 15 (see also paragra...
See Diagram 2.1c. The dwellinghouse should have either of the following. a. Protected stairway – a...
All habitable rooms (excluding kitchens) should have either of the following. a. An emergency escap...
A lift shaft serving storeys above ground level should not serve any basement, if either of the foll...
See Diagram 2.1d. In addition to meeting the provisions in paragraph 2.5, the dwellinghouse should c...
Basement storeys containing habitable rooms should have one of the following. a. An emergency escap...
In buildings with more than three storeys above the ground storey, stairs may serve the flats and ot...
The following paragraphs deal with means of escape from the entrance doors of flats to a final exit....
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
Where a storey or part of a building has multiple escape routes available, one may be over a flat ro...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
Buildings in which firefighting shafts should be provided, showing which storeys need to be served ...
Any external escape stair should meet all of the following conditions (Diagram 3.11). a. Doors to t...
If a building does not meet the criteria of paragraph 3.28, an escape stair forming part of the only...
Dwellinghouses with one internal stair should comply with paragraphs 2.5 and 2.6. In dwellinghouses ...
Further guidance on the construction of firefighting stairs is given in Section 15 (see also paragra...
See Diagram 2.1c. The dwellinghouse should have either of the following. a. Protected stairway – a...
All habitable rooms (excluding kitchens) should have either of the following. a. An emergency escap...
A lift shaft serving storeys above ground level should not serve any basement, if either of the foll...
See Diagram 2.1d. In addition to meeting the provisions in paragraph 2.5, the dwellinghouse should c...
Basement storeys containing habitable rooms should have one of the following. a. An emergency escap...
In buildings with more than three storeys above the ground storey, stairs may serve the flats and ot...
The following paragraphs deal with means of escape from the entrance doors of flats to a final exit....
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
Where a storey or part of a building has multiple escape routes available, one may be over a flat ro...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
Buildings in which firefighting shafts should be provided, showing which storeys need to be served ...