Buildings in which firefighting shafts should be provided, showing which storeys need to be served >18m >10m a. Any building The upper storeys in any building with a storey more than 18m above fire service vehicle access level b. Any building The basement storeys in any building with a basement more than 10m below fire service vehicle access level c. Any building The basement storey(s) in any building with two or more basements each exceeding 900m2 Fire service vehicle access level Two or more basement storeys each exceeding 900m2 Extent of firefighting Extent of firefighting lift stair NOTES: 1.Height excludes any top storey(s) consisting exclusively of plant rooms. 2.Firefighting shafts should serve all floors through which they...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
For some low rise buildings, the provisions in paragraphs 3.26 and 3.27 may be modified and the use ...
A building with basement storeys should have firefighting shafts in accordance with the following. ...
Minimum fire resistance REI60 from both sides with E30 Sa fire doors Minimum fire resistance REI 12...
Buildings with firefighting shafts should have fire mains provided in both of the following. a. The...
Firefighting stairs and firefighting lifts should be approached from either of the following. a. A...
No fire resistance required for door 1100mm zone above top landing 1100mm zone above top landing ...
The flights and landings of escape stairs should be constructed of materials achieving class A2-s3, ...
See Diagram 2.1d. In addition to meeting the provisions in paragraph 2.5, the dwellinghouse should c...
A lift shaft serving storeys above ground level should not serve any basement, if either of the foll...
6.—(1) The responsible person in relation to a high-rise residential building must prepare a plan fo...
See Diagram 2.1c. The dwellinghouse should have either of the following. a. Protected stairway – a...
Smoke outlets connecting directly to the open air should be provided from every basement storey, exc...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
For some low rise buildings, the provisions in paragraphs 3.26 and 3.27 may be modified and the use ...
A building with basement storeys should have firefighting shafts in accordance with the following. ...
Minimum fire resistance REI60 from both sides with E30 Sa fire doors Minimum fire resistance REI 12...
Buildings with firefighting shafts should have fire mains provided in both of the following. a. The...
Firefighting stairs and firefighting lifts should be approached from either of the following. a. A...
No fire resistance required for door 1100mm zone above top landing 1100mm zone above top landing ...
The flights and landings of escape stairs should be constructed of materials achieving class A2-s3, ...
See Diagram 2.1d. In addition to meeting the provisions in paragraph 2.5, the dwellinghouse should c...
A lift shaft serving storeys above ground level should not serve any basement, if either of the foll...
6.—(1) The responsible person in relation to a high-rise residential building must prepare a plan fo...
See Diagram 2.1c. The dwellinghouse should have either of the following. a. Protected stairway – a...
Smoke outlets connecting directly to the open air should be provided from every basement storey, exc...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
For some low rise buildings, the provisions in paragraphs 3.26 and 3.27 may be modified and the use ...