Minimum fire resistance REI60 from both sides with E30 Sa fire doors Minimum fire resistance REI 120 from accommodation side and REI60 from inside the shaft with E60 Sa fire doors NOTES: 1.Outlets from a fire main should be located in the firefighting lobby or, in the case of a shaft serving flats, in the firefighting stairway (see Diagram b). 2.Smoke control should be provided in accordance with BS9999 or, where the firefighting shaft only serves flats, the provisions for smoke control given in paragraph 3.49 may be followed instead. 3.A firefighting lift is required if the building has a floor more than 18m above, or more than 10m below, fire service vehicle access level. 4.This diagram is only to illustrate the basic components and...
Smoke vents should comply with one of the following. a. They should be located on an external wall ...
Any external escape stair should meet all of the following conditions (Diagram 2.7). a. Doors to th...
The outlets from fire mains should be located within the protected stairway enclosure (see Diagram 1...
Buildings in which firefighting shafts should be provided, showing which storeys need to be served ...
Firefighting shafts should achieve a minimum fire resistance of REI 120. A minimum of REI 60 is acce...
No fire resistance required for door 1100mm zone above top landing 1100mm zone above top landing ...
A building with a storey more than 18m above the fire and rescue service vehicle access level should...
Fire resisting window(minimum RE30) No fire resistance required for door 1100mm zone above top la...
Buildings with firefighting shafts should have fire mains provided in both of the following. a. The...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
a. CORRIDOR ACCESS WITHOUT DEAD ENDS b. CORRIDOR ACCESS WITH DEAD ENDS The central door may be omi...
Fire resistance to protected shaft to be a maximum of REI 60 Fire resistance of construction to be ...
The external wall of a protected shaft does not normally need to have fire resistance. Situations wh...
Smoke vents should comply with one of the following. a. They should be located on an external wall ...
Any external escape stair should meet all of the following conditions (Diagram 2.7). a. Doors to th...
The outlets from fire mains should be located within the protected stairway enclosure (see Diagram 1...
Buildings in which firefighting shafts should be provided, showing which storeys need to be served ...
Firefighting shafts should achieve a minimum fire resistance of REI 120. A minimum of REI 60 is acce...
No fire resistance required for door 1100mm zone above top landing 1100mm zone above top landing ...
A building with a storey more than 18m above the fire and rescue service vehicle access level should...
Fire resisting window(minimum RE30) No fire resistance required for door 1100mm zone above top la...
Buildings with firefighting shafts should have fire mains provided in both of the following. a. The...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
See paras 3.27 and 3.36 NOTES: 1. The arrangements shown also apply to the top storey. 2. See Dia...
a. SMALL SINGLE STAIR BUILDING *If smoke control is provided in the lobby, the travel distance can ...
a. CORRIDOR ACCESS WITHOUT DEAD ENDS b. CORRIDOR ACCESS WITH DEAD ENDS The central door may be omi...
Fire resistance to protected shaft to be a maximum of REI 60 Fire resistance of construction to be ...
The external wall of a protected shaft does not normally need to have fire resistance. Situations wh...
Smoke vents should comply with one of the following. a. They should be located on an external wall ...
Any external escape stair should meet all of the following conditions (Diagram 2.7). a. Doors to th...
The outlets from fire mains should be located within the protected stairway enclosure (see Diagram 1...