An alternative approach to that described in paragraph 2.21 would be to comply with all of the following. a. Provide sprinkler protection to the open-plan areas. b. Provide a fire resisting partition (minimum REI 30) and door (minimum E 20) to separate the ground storey from the upper storeys. The door should allow occupants of the loft room access to a first storey escape window. c. Separate cooking facilities from the open-plan area with fire resisting construction (minimum REI 30)
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
Refuse chutes and rooms for storing refuse should meet both of the following conditions. a. Be sepa...
Any external escape stair should meet all of the following conditions (Diagram 2.7). a. Doors to th...
Where a new storey is added through conversion to create a storey above 4.5m, both of the following ...
Where adding an additional storey to a two storey single family dwellinghouse, new floors should hav...
See Diagram 2.1d. In addition to meeting the provisions in paragraph 2.5, the dwellinghouse should c...
See Diagram 2.1c. The dwellinghouse should have either of the following. a. Protected stairway – a...
When multi-storey flats do not have their own external entrance at ground level, adopt one of the fo...
Dwellinghouses with one internal stair should comply with paragraphs 2.5 and 2.6. In dwellinghouses ...
Where access from any habitable room to the entrance hall or flat entrance is impossible without pas...
One of the following approaches should be adopted, observing the inner room restrictions described i...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
NOTE: The ceiling should meet the following conditions. a. Provide a minimum fire resistance of EI...
All habitable rooms (excluding kitchens) should have either of the following. a. An emergency escap...
Where a flat roof forms part of a means of escape, it should comply with all of the following. a. I...
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
Refuse chutes and rooms for storing refuse should meet both of the following conditions. a. Be sepa...
Any external escape stair should meet all of the following conditions (Diagram 2.7). a. Doors to th...
Where a new storey is added through conversion to create a storey above 4.5m, both of the following ...
Where adding an additional storey to a two storey single family dwellinghouse, new floors should hav...
See Diagram 2.1d. In addition to meeting the provisions in paragraph 2.5, the dwellinghouse should c...
See Diagram 2.1c. The dwellinghouse should have either of the following. a. Protected stairway – a...
When multi-storey flats do not have their own external entrance at ground level, adopt one of the fo...
Dwellinghouses with one internal stair should comply with paragraphs 2.5 and 2.6. In dwellinghouses ...
Where access from any habitable room to the entrance hall or flat entrance is impossible without pas...
One of the following approaches should be adopted, observing the inner room restrictions described i...
If the fire resisting construction of a protected escape route is either of the following. a. Not c...
NOTE: The ceiling should meet the following conditions. a. Provide a minimum fire resistance of EI...
All habitable rooms (excluding kitchens) should have either of the following. a. An emergency escap...
Where a flat roof forms part of a means of escape, it should comply with all of the following. a. I...
Provisions for the fire properties of roofs are given in other parts of this document. a. Requireme...
Refuse chutes and rooms for storing refuse should meet both of the following conditions. a. Be sepa...
Any external escape stair should meet all of the following conditions (Diagram 2.7). a. Doors to th...