From analisys of data, value of efficiency percentage and losses that generated in transformer 54 MVA at PT. PLN (Persero) Keramasan Power Plant. To know value of efficiency and losses of transformer 54 MVA PLN Keramasan got from manual calculation. The calculation by manual is did with collect the data like input power and current of load used in transformer. In manual calculation, output power in highest load is 33715 KW, in average load is 50.831 and in smallest load is 38.843. The smallest total losses when the smallest load is 156,861 KW and the biggest losses total when the biggest load is 134,827 KW. The biggest efficiency in transformer PLN Keramasan is got from when the smallest load is 99,59 %, and the smallest efficiency is got ...
Setiap operasi transformator yang digunakan untuk penyaluran listrik terdapat rugi-rugi. Rugi-rugi ...
A transformer is a device that uses the principle of magnetic-induction work simply, reliably, and e...
Distribution transformer which has been burdened need to know how much load is already installed on ...
From analisys of data, value of efficiency percentage and losses that generated in transformer 80 MV...
Berdasarkan hasil pembahasan, besar nilairugi-rugi, daya output danefisiensiyang dihasilkan transfor...
In the industry, the load of transformer usually varies. So when the load of transformer was changi...
Besar kecilnya efisiensi yang dihasilkan oleh transformator dipengaruhi oleh besar kecilnya pembeban...
Dalam suatu pelayanan daya listrik maka diperlukan transformator , transformator efisiensinya harus ...
Untuk mengkonversikan energi listrik diperlukan peralatan listrik pendukung, diantara nya adalah tra...
This study aims to determine the magnitude of the fluctuating load factor on the efficiency and loss...
Transformer is a device that can increase of decreae a voltage. The transformer used in the diesel p...
Efficiency transformer was calculated at the time of transformer is being operating normally. Calcul...
This study aims to determine the magnitude of the fluctuating load factor on the efficiency and loss...
The efficiency level of the transformer becomes a benchmark to determine the optimal performance of ...
Maintenance is an important function that is important in a company. A production plan may fail if t...
Setiap operasi transformator yang digunakan untuk penyaluran listrik terdapat rugi-rugi. Rugi-rugi ...
A transformer is a device that uses the principle of magnetic-induction work simply, reliably, and e...
Distribution transformer which has been burdened need to know how much load is already installed on ...
From analisys of data, value of efficiency percentage and losses that generated in transformer 80 MV...
Berdasarkan hasil pembahasan, besar nilairugi-rugi, daya output danefisiensiyang dihasilkan transfor...
In the industry, the load of transformer usually varies. So when the load of transformer was changi...
Besar kecilnya efisiensi yang dihasilkan oleh transformator dipengaruhi oleh besar kecilnya pembeban...
Dalam suatu pelayanan daya listrik maka diperlukan transformator , transformator efisiensinya harus ...
Untuk mengkonversikan energi listrik diperlukan peralatan listrik pendukung, diantara nya adalah tra...
This study aims to determine the magnitude of the fluctuating load factor on the efficiency and loss...
Transformer is a device that can increase of decreae a voltage. The transformer used in the diesel p...
Efficiency transformer was calculated at the time of transformer is being operating normally. Calcul...
This study aims to determine the magnitude of the fluctuating load factor on the efficiency and loss...
The efficiency level of the transformer becomes a benchmark to determine the optimal performance of ...
Maintenance is an important function that is important in a company. A production plan may fail if t...
Setiap operasi transformator yang digunakan untuk penyaluran listrik terdapat rugi-rugi. Rugi-rugi ...
A transformer is a device that uses the principle of magnetic-induction work simply, reliably, and e...
Distribution transformer which has been burdened need to know how much load is already installed on ...