The work covers the electromagnetic transients at one-phase earths in the cable networks 6 - 10 kV and also the signalling devices of one-phase earths. The analytical solutions for equations of the transients at one-phase earths in the compensated and non-compensated cable networks and also the principles for construction of the signalling and registaration devices of one-phase earths have been proposed. The device complex ("TEMP-1", "Impuls", signalling and registration devices of one-phase earths) possessing the more high technical improvement in comparison with the actual devices of analogous purpose has been developed. More than 80 device sets "TEMP-1" and "Impuls" have been introduced in the elec...
This article deals with selective protection against single-phase earth faults at 6 – 10 kV electri...
The relevance of the stated topic of scientific research is determined by the importance of the elem...
There tne mathematical models to study the transient conditions in three-phase ahd two-phase short c...
Single-phase earth faults are the predominant type of damage in distribution 6-10 kV cable networks,...
The experimental investigations on the physical models, theoretical analysis, computer mathematical ...
The electromagnetic transients in the electric power systems and earthing protection devices in the ...
Abstract-Protections based by higher harmonics absolute measurements the zero sequence currents of t...
The investigation is concerned with power supply systems featuring neutral point different modes. Th...
The new indirect methods determining the conductances of earth network phase and also the compensati...
The work covers the electrotechnical complexes (ETC) and systems of opencasting (OC). The system ana...
The paper demonstrates improving the reliability of power supply and operating safety of power recei...
The main objectives of this publication are: 1) to attract the attention of energy specialists to th...
New algorithms have been developed for selective protection against phase-to-earth faults in power s...
Subject of investigation: underground conductors and cable communication lines. Purpose of the work:...
The article shows the power quality indicators that are most important for electric consumers: high ...
This article deals with selective protection against single-phase earth faults at 6 – 10 kV electri...
The relevance of the stated topic of scientific research is determined by the importance of the elem...
There tne mathematical models to study the transient conditions in three-phase ahd two-phase short c...
Single-phase earth faults are the predominant type of damage in distribution 6-10 kV cable networks,...
The experimental investigations on the physical models, theoretical analysis, computer mathematical ...
The electromagnetic transients in the electric power systems and earthing protection devices in the ...
Abstract-Protections based by higher harmonics absolute measurements the zero sequence currents of t...
The investigation is concerned with power supply systems featuring neutral point different modes. Th...
The new indirect methods determining the conductances of earth network phase and also the compensati...
The work covers the electrotechnical complexes (ETC) and systems of opencasting (OC). The system ana...
The paper demonstrates improving the reliability of power supply and operating safety of power recei...
The main objectives of this publication are: 1) to attract the attention of energy specialists to th...
New algorithms have been developed for selective protection against phase-to-earth faults in power s...
Subject of investigation: underground conductors and cable communication lines. Purpose of the work:...
The article shows the power quality indicators that are most important for electric consumers: high ...
This article deals with selective protection against single-phase earth faults at 6 – 10 kV electri...
The relevance of the stated topic of scientific research is determined by the importance of the elem...
There tne mathematical models to study the transient conditions in three-phase ahd two-phase short c...