The water level in the steam drum needs to be kept constant at a certain point. Therefore, control is needed for the flow rate of incoming water feedwater to adjust to the disruption of the steam flow rate that comes out. The size of the steam flow rate that comes out depends on the load demand. If the demand for loads is high and fluctuations, then the water level in the steam drum will be more difficult. The PID type fuzzy logic controller with a robust self-tuning scheme will be implemented in the water level regulation system in the steam drum. In the three-element control scheme, when given a high load of 700 MW the system produces an error deviation of 15.69 mm peak against the set point. This value is smaller than the single-element ...