The objective of the present study is to investigate the efficiency of indirect adiabatic chiller-based cooling system efficiency dependence of outdoor air humidity. The system is located in historical building, in temperate climate of Latvia. The data about electricity consumption, water consumption, chiller operation stages, cooling average temperatures, and outdoor air parameters have been acquired for the period of 2,5 month, during the cooling season. Using data collected by BACnet based BMS controllers and adiabatic chiller control system, we have analyzed operation efficiency of the chiller and its dependence of outdoor air humidity. Data range for the period from 1st August till 13th of October, year 2011 was taken for deeper analy...
Strategy of the European Union in efficient energy usage demands to have a higher proportion of rene...
The indoor climate in historic buildings is crucial in order to the preserve the building, interiors...
Purpose: The operation of chiller systems could account for considerable electricity consumption in ...
The present study is devoted to the evaluation of efficiency of the combined indirect evaporative – ...
The present study is devoted to efficiency evaluation of a combined indirect evaporative – compresso...
In an indirect evaporative air cooling (IEAC) installation air is cooled by means of adiabatic humid...
The prices for energy resources, global trends for greenhouse gases emission limitation makes the ap...
In an indirect evaporative air cooling (IEAC) installation air is cooled by means of adiabatic humid...
There are 320 historical cult buildings as cultural monuments of national significance in Latvia. Cu...
As building energy consumption gains ever-increasing attention worldwide, the focus on addressing it...
The level of human occupancy in historic religious buildings influences the internal heat gains and...
In many historic buildings, conservation heating has been used to control the RH in winter. Heat pum...
In article the review of the information on possibilities of use of recuperators of heat is presente...
This paper describes ventilation, the air conditioning and its control system’s development for arch...
This study demonstrates how to compare the energy performance of an existing air-cooled chiller with...
Strategy of the European Union in efficient energy usage demands to have a higher proportion of rene...
The indoor climate in historic buildings is crucial in order to the preserve the building, interiors...
Purpose: The operation of chiller systems could account for considerable electricity consumption in ...
The present study is devoted to the evaluation of efficiency of the combined indirect evaporative – ...
The present study is devoted to efficiency evaluation of a combined indirect evaporative – compresso...
In an indirect evaporative air cooling (IEAC) installation air is cooled by means of adiabatic humid...
The prices for energy resources, global trends for greenhouse gases emission limitation makes the ap...
In an indirect evaporative air cooling (IEAC) installation air is cooled by means of adiabatic humid...
There are 320 historical cult buildings as cultural monuments of national significance in Latvia. Cu...
As building energy consumption gains ever-increasing attention worldwide, the focus on addressing it...
The level of human occupancy in historic religious buildings influences the internal heat gains and...
In many historic buildings, conservation heating has been used to control the RH in winter. Heat pum...
In article the review of the information on possibilities of use of recuperators of heat is presente...
This paper describes ventilation, the air conditioning and its control system’s development for arch...
This study demonstrates how to compare the energy performance of an existing air-cooled chiller with...
Strategy of the European Union in efficient energy usage demands to have a higher proportion of rene...
The indoor climate in historic buildings is crucial in order to the preserve the building, interiors...
Purpose: The operation of chiller systems could account for considerable electricity consumption in ...