This study investigates numerically the occurrence and duration of higher relative humidities in a cold attic space, which are a consequence of the excessive moisture supply from the ventilation of the attic and from the infiltration of air from a dwelling. Hygrothermal states of the attic air zone and of the adjacent construction elements are calculated by a whole building heat, air and moisture simulation tool. Airflows to the attic are determined by taking into account the total distribution of pressure around and inside a building. The role of the attic ventilation is analyzed by comparing naturally ventilated and unventilated attics in an open landscape or in a city zone. For the air infiltration from the dwelling only scenarios with t...
Ventilated roofs with an air space above the upper floor insulation inherently are more prone to moi...
This study was done regarding whether sealing or ventilation is the best solution to prevent moistur...
In this thesis project, the air and heat flow in a principal insulated cold attic model has been num...
This paper deals with a common moisture problem in Swedish houses – the occurrence of high moisture ...
Cold ventilated attics often have mould problems in Sweden. This is valid both for old and sometimes...
Damages, caused by moisture and mould, in cold attics have increased in Sweden during the last decad...
Most of the last 20 years in Sweden have been mild and wet compared to the 1961–1990 climate referen...
airtightness, wind pressure coefficients and the positions of leakage paths have to be made. One poi...
Damages, caused by moisture and mould, in attics have increased in Sweden during the last decades. T...
In this Master's thesis, numerical modeling of transient air, heat and mass transport is investigate...
Damages, caused by moisture and mould, in cold attics have increased in Sweden during the last decad...
Tougher fire requirements and the desire to make simpler designs have enabled construction companies...
The reality of the effect of natural ventilation in a residential attic cavity has been the topic of...
To remove moisture by ventilating constructions is a well-known strategy, used successfully in numer...
Attic air temperature of wooden houses usually rises more than 50°C during daytime in the summer sea...
Ventilated roofs with an air space above the upper floor insulation inherently are more prone to moi...
This study was done regarding whether sealing or ventilation is the best solution to prevent moistur...
In this thesis project, the air and heat flow in a principal insulated cold attic model has been num...
This paper deals with a common moisture problem in Swedish houses – the occurrence of high moisture ...
Cold ventilated attics often have mould problems in Sweden. This is valid both for old and sometimes...
Damages, caused by moisture and mould, in cold attics have increased in Sweden during the last decad...
Most of the last 20 years in Sweden have been mild and wet compared to the 1961–1990 climate referen...
airtightness, wind pressure coefficients and the positions of leakage paths have to be made. One poi...
Damages, caused by moisture and mould, in attics have increased in Sweden during the last decades. T...
In this Master's thesis, numerical modeling of transient air, heat and mass transport is investigate...
Damages, caused by moisture and mould, in cold attics have increased in Sweden during the last decad...
Tougher fire requirements and the desire to make simpler designs have enabled construction companies...
The reality of the effect of natural ventilation in a residential attic cavity has been the topic of...
To remove moisture by ventilating constructions is a well-known strategy, used successfully in numer...
Attic air temperature of wooden houses usually rises more than 50°C during daytime in the summer sea...
Ventilated roofs with an air space above the upper floor insulation inherently are more prone to moi...
This study was done regarding whether sealing or ventilation is the best solution to prevent moistur...
In this thesis project, the air and heat flow in a principal insulated cold attic model has been num...